Hi everyone!
I’m trying to use PMU Connection Tester V4.7.4 to communicate with a PMU Unit, make Siemens Siprotec model 7SJ82. The device support C37.118.1a-2014 protocol version. Do you think it will be possible to communicate this version of the Tester with that PMU unit?. I’ve tried with UDP variant with no success; everytime the PMU closes the communication at the first attempt.
Thanks a lot!
The “.1” standards of the IEEE protocol describe the metrology of phasors, not their broadcast, i.e., data reporting; this is handled by the “.2” versions of the protocol. These are the currently published reporting standards:
IEEE C37.118-2005
: Metrology + Reporting in same document
IEEE C37.118.2-2011
: Reporting only, Metrology moved to “.1” document
IEEE C37.118.2-2024
: Reporting only - standard still pending publication
Note that UDP communications can be tricky - make sure to firewalls allow communications.
Hope that helps!
Thanks,
Ritchie